Page 1 of 1

Generator Feed Cable gauge

Posted: Tue Aug 12, 2014 6:55 pm
by jtalberts
I have been trying to figure this out for a few weeks now and I haven't found a great answer. My new genset is rated as such

Model: 8.0 SBEG
Volts: 120/240
Amps: 66/33
Hertz: 60
Phase: 1
Wire: 4
P.F.: 1.0
KW: 8.0
RPM: 1800

It will be located in my engine compartment and the run will be roughly 35-40ft. Also, my old genset only had 3 cables running from it. Will this one have 4?

Re: Generator Feed Cable gauge

Posted: Sun Aug 17, 2014 11:16 am
by Roger2
You should only need 3 conductors if you use 240 volt. If you would email me a copy of connection diagram I can help you. Former Coal mine chief elect.
Roger

Re: Generator Feed Cable gauge

Posted: Mon Feb 09, 2015 1:52 pm
by Dougrose
240 Volt normally has 4 conductors:

Red: hot
Black: hot
White: neutral
Green: ground

Re: Generator Feed Cable gauge

Posted: Tue Feb 10, 2015 3:34 pm
by bill
BigM
I have never seen a Marinette with 240 volt :!: Most would be 120 volt with 3 wire, white common, black hot and green ground similar to your home wiring.
bill

Re: Generator Feed Cable gauge

Posted: Sat Feb 21, 2015 1:46 pm
by Dougrose
Please note that, within the engine room, allowed current for 8 AWG wire is 68 A. and that is what you should use if you wire for 110 V. output.

Allowed current for 12 AWG is 38.3 A., and that is what you should use if you wire for 220 V. output, using the four wire arrangement.

If you have NO 120 V. loads, you could leave off the neutral white wire, but it is probably a bad idea.

I am not sure how your boat is wired, but if it were on my boat, I would wire for 120 V output and put two 30 A. breakers at the generator, and wire one to your AC panel using 12 AWG wire, and one to your 120 V air conditioner or whatever other load you use, also using 12 AWG wire. There are two 120 V windings on the generator, and you could wire each winding to its own breaker. If you have a mix of 120 V and 240 V loads, then things get a little more complicated. Time to send that diagram to Roger.

Re: Generator Feed Cable gauge

Posted: Sat Feb 21, 2015 3:35 pm
by Roger2
Dough,
You are correct on the Green Ground, I was only county actual conductors, with ground understood.
Great to see you back on site.

Roger

Re: Generator Feed Cable gauge

Posted: Sat Feb 21, 2015 3:39 pm
by jtalberts
I will get a diagram made up and posted.I am finally getting back to this project.